Asked by patricktam
at 2024-07-14 02:59:58
Point:500 Replies:3 POST_ID:828973USER_ID:11873
Topic:
Computer Servers;Components;Miscellaneous Hardware
I am a bit new on data center infrastructure design so kindly bare with me.
Our company are provisioning a new infrastructure project and currently concerning about Rack Space allocation and most importantly power consumption estimation with details as follows:
We are purchasing a new Server Rack Cabinet with will contain 2 HP DL380 Gen8 Servers together with Two Cisco 2960x network Switches. Also, we will install LCD Console on the Rack. We need to calculate the "Total Power Required" for this configuration in (kVA) for our data center's staff power consumption allocation.
Kindly advice how to estimate the power in (kVA) for the above configuration ?
Greatly appreciate your advice in advance.
Regards
Patrick T.
Our company are provisioning a new infrastructure project and currently concerning about Rack Space allocation and most importantly power consumption estimation with details as follows:
We are purchasing a new Server Rack Cabinet with will contain 2 HP DL380 Gen8 Servers together with Two Cisco 2960x network Switches. Also, we will install LCD Console on the Rack. We need to calculate the "Total Power Required" for this configuration in (kVA) for our data center's staff power consumption allocation.
Kindly advice how to estimate the power in (kVA) for the above configuration ?
Greatly appreciate your advice in advance.
Regards
Patrick T.
Author: patricktam replied at 2024-07-14 06:33:15
Thank you guys for given me such great hint. Appreciate your help.
Expert: duncanb7 replied at 2024-07-14 03:43:18
Did you read this before from HP for HP Power Calculators that also include DL380 Gen8 server ?
http://h20566.www2.hp.com/portal/site/hpsc/template.PAGE/public/kb/docDisplay/?spf_p.tpst=kbDocDisplay&spf_p.prp_kbDocDisplay=wsrp-navigationalState%3DdocId%253Demr_na-c01510445-11%257CdocLocale%253D%257CcalledBy%253D&javax.portlet.begCacheTok=com.vignette.cachetoken&javax.portlet.endCacheTok=com.vignette.cachetoken
Download hp power adviosr software to see it is useful or not for your case and it is just a test only
http://www8.hp.com/us/en/products/servers/solutions.html?compURI=1439951#.U8OwSflH9Zc
Hope understand your question completely.If not, please point it out
Duncan
http://h20566.www2.hp.com/portal/site/hpsc/template.PAGE/public/kb/docDisplay/?spf_p.tpst=kbDocDisplay&spf_p.prp_kbDocDisplay=wsrp-navigationalState%3DdocId%253Demr_na-c01510445-11%257CdocLocale%253D%257CcalledBy%253D&javax.portlet.begCacheTok=com.vignette.cachetoken&javax.portlet.endCacheTok=com.vignette.cachetoken
Download hp power adviosr software to see it is useful or not for your case and it is just a test only
http://www8.hp.com/us/en/products/servers/solutions.html?compURI=1439951#.U8OwSflH9Zc
Hope understand your question completely.If not, please point it out
Duncan
Accepted Solution
Expert: Kimputer replied at 2024-07-14 03:23:55
500 points EXCELLENT
DL380G8 can operate on a single 480W PSU (usually 480W when all HDD bays are in use, a bit lower when less HDD's and PCI/X/e expansions)
Those Cisco switches operate on either 30 or 15W per port (depends on your version).
The LCD console is just a wild guess, probably around 100W.
Now add these together and you have at least a nice max value.
Example max
fully loaded DL380's = 2 x 480W = 960W
48 PoE devices at 30W = 1440W
LCD console = 100W
total = 2500W (roughly around 2.5kVA)
Those Cisco switches operate on either 30 or 15W per port (depends on your version).
The LCD console is just a wild guess, probably around 100W.
Now add these together and you have at least a nice max value.
Example max
fully loaded DL380's = 2 x 480W = 960W
48 PoE devices at 30W = 1440W
LCD console = 100W
total = 2500W (roughly around 2.5kVA)